lightecho said "I agree with you FPP1. The forms we use don't really allow you to address non 25 issues except in "Recommendations". The question though, what happens when you find a 25 issue that was caused by the installation in the first place?"
You don't know what happened.
As an example:
NFPA 13R Section 6.6.7.1.3 Listed quick-response sprinklers shall be permitted to be installed in dwelling units meeting the definition of a compartment, as defined in Section 4.1, where no more than four sprinklers are located in the dwelling unit.
A few years back I did a single story apartment building, in an extremely cold northern climate, and I wanted to use quick response dry pendent sprinklers on a dry pipe system. Problem was as hard as I tried I needed five sprinklers per dwelling unit which would obviously be incorrect.
The culprit was the sprrinkler required in a small (8 sq. ft.) mechanical closet containing equipment only feeding the dwelling unit that was placed along an outside wall.
The state the project was located was a mini/maxi state. The local authority could not accept less, nor could they require more, than what was exactly in the adopted standard. but they did have a "Board of Building Standards" made up of eight people appointed by the Governor who could pretty much do anything they wanted under state law but first drawings had to be submitted, rejected and then you could file an appeal.
So when dropping the plans off I told the local plan examiner I fully expected a rejection explaining the problem and that I wanted to appeal.
Plans were rejected on the spot.
Filed the appeal, explained the problem to the board, the architect explained the doors to the mechanical closets were always locked and how the occupants did not have keys.
Nobody objected, I got the varience (on official state leterhead) and the job was done in full compliance with the approved plans and state law.
I want to point out the board was made up of two engineers, one architect, two lawyers, a high school teacher and a couple moms who appeared bored with nothing else to do.
So what does an inspector say when he counts five dry pendent sprinklers in a dwelling unit?
The answer is nothing... he has to assume the original installation was installed per code, inspected and approved which it was.
I have to think there's lots and lots of jobs exactly like this one.
I am expecting an angry phone call from the owner some day but I still have the paperwork.