Oct 22, 2018 #1 sl3656 Mechanical Joined Sep 14, 2018 Messages 37 Location US As mentioned in the title of this post, should the dry-pipe main and auxiliary drain piping be included as part of the dry-pipe system volume calculation? I believe it should be, but would appreciate a second opinion.
As mentioned in the title of this post, should the dry-pipe main and auxiliary drain piping be included as part of the dry-pipe system volume calculation? I believe it should be, but would appreciate a second opinion.
Oct 22, 2018 #2 TravisMack Mechanical Joined Sep 15, 2003 Messages 1,776 Location US I always include them up to the system side of the drain valve. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Upvote 0 Downvote
I always include them up to the system side of the drain valve. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Oct 22, 2018 #3 SprinklerDesigner2 Mechanical Joined Nov 30, 2006 Messages 1,281 Location US Travis does it right. Total volume. Upvote 0 Downvote
Oct 23, 2018 Thread starter #4 sl3656 Mechanical Joined Sep 14, 2018 Messages 37 Location US Thanks for the replies guys. Thought so! Upvote 0 Downvote