jimmy2times
Electrical
- Jun 26, 2007
- 138
we have 6.6kv induction motor for bow thruster of ship (1.4MW), difficult access for cleaning and removal.
we conduct PI insulation resistance measurements and have low PI reading ratio. 1min IR reading is just over 100Mohm though (102Mohm) so not awful by any means.
We ran anti condensation heaters for few days but no real improvement in result.
just wondering what the view is in terms of doing additional in situ testing in such case to determine condition of winding. I recall reading thread on here on Baker testing a while back and some advocating it with a Go/No-Go outcome, whilst others not. Just wondering if views are still the same or if any new developments out there in this space.
we conduct PI insulation resistance measurements and have low PI reading ratio. 1min IR reading is just over 100Mohm though (102Mohm) so not awful by any means.
We ran anti condensation heaters for few days but no real improvement in result.
just wondering what the view is in terms of doing additional in situ testing in such case to determine condition of winding. I recall reading thread on here on Baker testing a while back and some advocating it with a Go/No-Go outcome, whilst others not. Just wondering if views are still the same or if any new developments out there in this space.