I have a three phase pole mounted bank made out of 3 single phase transformers 100kVA 12470GrdY/7200-120/240V. The %Iz of each transformer is respectively 1.9%, 1.8% and 1.6% on the 100kVA base. The transformers are connected as a 12470GrdY-208GrdY bank (The 2 LV windings of each single phase unit are re-connected in parallel as 120V)
The consulting engineer for the building being serviced is requesting to have the actual % Iz of the above mentioned bank to calculate the S/C .... How do I calculate it in this case?
I read that if all 3 transformers had the same %Iz, lets say 1.9%, then the % Iz of the bank would be 1.9% (300kVA base).... but in this case each of the %Iz is quite different; can someone help and show the calculations to go through?
Thanks!