Even though wind farms are becoming common almost everywhere, they are mostly large scale connecting to HV transmission lines and appear much less common as imbedded distributed generation (DG) connecting to medium voltage distribution lines. Such distribution scenarios appear not to be well researched yet and available references such as IEEE P-1547 not particularly informative.
So, I’m working on a 10MW wind DG facility project connecting to a rural radial distribution line 44kV. The line originates from a 230/44kV substation. The 44kV line is about 40km long and the DG facility about 25km from the substation. There are residential loads about 5-10km downstream from the DG facility.
The DG facility is served by a switching station with a breaker and transfer trip (TT) scheme which interacts with upstream utility protections located at the substation and also a line recloser, which is about 10km upstream.
The teleprotection scheme uses a radio link. Upon detecting a fault, the utility will trip its own interrupting device (breaker or recloser) and also send a TT signal to the DG facility protection. Once TT signal is received and the DG facility breaker is tripped, a Distributed Generation End Open (DGEO) signal will be sent back to the utility, which enables their auto-recloser to attempt to restore the line.
This seems to work; however, the problem is the islanding condition which occurs when the utility interrupter is already tripped while the TT signal is still being processed before it trips the DG breaker, which may take about 100ms.
During this time consumers on the line will continue to be fed from the islanded DG, while the fault may or may not be isolated. Islanding condition may also occur when the utility interrupter is inadvertently opened and no TT signal is sent, line conductor broken far upstream, etc.
The specific problem is that according to the WT supplier, if an islanding condition occurs, the overvoltage which lasts several cycles may be over 2.0 pu before the turbine controller reacts and readjusts inverter output. Apparently, utility consumers still left on the line may be severely affected by a large overvoltage surge.
The WT supplier also states that such islanding condition leading to severe overvoltage problem should somehow be cleared within half of cycle which is technically impossible, unless the TT scheme is such that utility protections trip the DG facility first and then trip utility breaker or recloser.
This, however, is not acceptable to the utility as the tripping time for their instantaneous protections would probably reach some 200ms total, by the time TT signal is received at DG end, DG breaker open, and DGEO signal sent back.
Would anyone be able to provide some comments please.
So, I’m working on a 10MW wind DG facility project connecting to a rural radial distribution line 44kV. The line originates from a 230/44kV substation. The 44kV line is about 40km long and the DG facility about 25km from the substation. There are residential loads about 5-10km downstream from the DG facility.
The DG facility is served by a switching station with a breaker and transfer trip (TT) scheme which interacts with upstream utility protections located at the substation and also a line recloser, which is about 10km upstream.
The teleprotection scheme uses a radio link. Upon detecting a fault, the utility will trip its own interrupting device (breaker or recloser) and also send a TT signal to the DG facility protection. Once TT signal is received and the DG facility breaker is tripped, a Distributed Generation End Open (DGEO) signal will be sent back to the utility, which enables their auto-recloser to attempt to restore the line.
This seems to work; however, the problem is the islanding condition which occurs when the utility interrupter is already tripped while the TT signal is still being processed before it trips the DG breaker, which may take about 100ms.
During this time consumers on the line will continue to be fed from the islanded DG, while the fault may or may not be isolated. Islanding condition may also occur when the utility interrupter is inadvertently opened and no TT signal is sent, line conductor broken far upstream, etc.
The specific problem is that according to the WT supplier, if an islanding condition occurs, the overvoltage which lasts several cycles may be over 2.0 pu before the turbine controller reacts and readjusts inverter output. Apparently, utility consumers still left on the line may be severely affected by a large overvoltage surge.
The WT supplier also states that such islanding condition leading to severe overvoltage problem should somehow be cleared within half of cycle which is technically impossible, unless the TT scheme is such that utility protections trip the DG facility first and then trip utility breaker or recloser.
This, however, is not acceptable to the utility as the tripping time for their instantaneous protections would probably reach some 200ms total, by the time TT signal is received at DG end, DG breaker open, and DGEO signal sent back.
Would anyone be able to provide some comments please.