I suggest a simple approach by doing the following:
Find the energy carried by the magnet at the moment of hitting the wall. It will be kinetik but is equivalent to mass by vertical distance traveled before hitting. If you can estimate the hitting speed would be better, because in addition to vert travel, there could be some addinional energy imparted by the crane while turning.
Apply an unitary horizontal force to the wall at the point where it will be hit, and find the displacement of the wall at that point. If I'm not wrong, the energy absorbed by the wall will be the unitary force by one half the displacement, like in the elementary spring problem. Then multiply the unitary force by the quotient of both energy numbers and you have a static force to design the wall. I would say that dynamics consideration would surely be result in lower forces, so you would be on the safe side. Also remember material has additional capacity for dynamic loads. One more aspect is regarding the capacity design of the precast wall: If you want the wall to remain within service levels when hit or to break/yield and being replaced. Sorry for the deficient english, hope being understood and helpful.