burntcoil
Electrical
- Sep 28, 2011
- 75
I use to do CT sizing based on the available short circuit and see if the voltage developed on the secondary is less then my knee point voltage.
I have come accross instances where the above criteria meets but my CT does not meet the IEEE definition of "C" class CT. Please see below a practicle example.
CT Ratio 3000/5, Vk = 120V, IEEE Class C50
Fault Current = 35kA, Voltage developed on secondary for this fault current is 83.85V, which is much lower then the Knee Point voltage of the CT, so the CT is fine as per my understanding.
As per deifination C50 means for 20times rated current and 5A secondary my CT is suitable if my burden is 0.5ohm. i.e. 20 x 5 x 0.5 = 50
But in actual case my burden is 1.44Ohm, 35000 (11.66 of rated 3000A) and a secondary of 5A. So using above deifination of Class "C" CTs, I can determine the required IEEE Class i.e. 1.44 x 11.66 x 5 =84, so now I shall choose a CT of Class C100.
My question is that if my CT meets the Knee Point criteria, even then shall I look at the relaying class of the CT or that is not important.
OR
I have to meet both the Knee point criteria as well as Relaying Class as well.
Thanks in advance for your responses.
I have come accross instances where the above criteria meets but my CT does not meet the IEEE definition of "C" class CT. Please see below a practicle example.
CT Ratio 3000/5, Vk = 120V, IEEE Class C50
Fault Current = 35kA, Voltage developed on secondary for this fault current is 83.85V, which is much lower then the Knee Point voltage of the CT, so the CT is fine as per my understanding.
As per deifination C50 means for 20times rated current and 5A secondary my CT is suitable if my burden is 0.5ohm. i.e. 20 x 5 x 0.5 = 50
But in actual case my burden is 1.44Ohm, 35000 (11.66 of rated 3000A) and a secondary of 5A. So using above deifination of Class "C" CTs, I can determine the required IEEE Class i.e. 1.44 x 11.66 x 5 =84, so now I shall choose a CT of Class C100.
My question is that if my CT meets the Knee Point criteria, even then shall I look at the relaying class of the CT or that is not important.
OR
I have to meet both the Knee point criteria as well as Relaying Class as well.
Thanks in advance for your responses.