IEEE 80-2000 Table-7 Typo

Status
Not open for further replies.

HectorSM

Electrical
Joined
Oct 20, 2010
Messages
2
Location
MX
IEEE Std-80-2000 has 10,000 Ohm-m for wet gravel in Table-7, while IEEE Std-142-2007 has 1,000 Ohm-m in Table-4.2.
Is this a typo in Table-7 Std-80-2000 which gives un unsafe result by allowing a smaller substation grounding grid?

 