In calculating the arc flash hazard on a bus with 2 sources, does one calculate the incident energy contribution from each source seperately and then add them to get the total energy?
For example:
Source A: 3.5 cal/cm2 @ 18" working distance and arc flash boundary is 32"
Source B: 3.9 cal/cm2 @ 18" working distance and AFB is 40"
Would the total arc flash hazard be 7.4 cal/cm2 @ 18"?
What would the arc flash boundary then be? 40" or 72" ?
I could not find anything in IEEE 1584 on this but I believe it would add. Thank You for a sanity check.
For example: