radug
Electrical
- May 23, 2007
- 105
Hello,
I have some questions that I think are related to thread238-289927 but it is closed.
squasher,
In your first post, shouldn't it be used Ith instead of Ik for short-time withstand current in 3 seconds?
It is a question I have about IEC 60909 because if Ith should be used, then I do not know what is the use of Ik related to switchgear rating. I think it would be used only for protective device coordination purposes.
And about motor contribution, IEC 60909 says that they must be considered when doing maximum short-circuit calculations and discarded when doing minimum short-circuit calculations. Correct me if I am wrong, but I think that:
-Maximum short circuit: use ip, Ith(1sec or 3sec) for busbar rating, and addionaly Ib for circuit-breaker breaking current rating. So, no use for Ik.
-Miniumum short circuit: Ik for protection device coordination, but as with mimumum motors are neglected it does not calculate motor contribution so when setting motor-protection relays, Ik of the maximum short circuit should be used.
Last, I have been looking for a reference in the standard or other place about asynchronous motor behaviour during short-circuit: why consider contribution for maximum short-circuit and not for minimum? during how much time does the motor contribution last during short-circuit? if it stops, why? because it breaks, because it self-stops?
I have some questions that I think are related to thread238-289927 but it is closed.
squasher,
In your first post, shouldn't it be used Ith instead of Ik for short-time withstand current in 3 seconds?
It is a question I have about IEC 60909 because if Ith should be used, then I do not know what is the use of Ik related to switchgear rating. I think it would be used only for protective device coordination purposes.
And about motor contribution, IEC 60909 says that they must be considered when doing maximum short-circuit calculations and discarded when doing minimum short-circuit calculations. Correct me if I am wrong, but I think that:
-Maximum short circuit: use ip, Ith(1sec or 3sec) for busbar rating, and addionaly Ib for circuit-breaker breaking current rating. So, no use for Ik.
-Miniumum short circuit: Ik for protection device coordination, but as with mimumum motors are neglected it does not calculate motor contribution so when setting motor-protection relays, Ik of the maximum short circuit should be used.
Last, I have been looking for a reference in the standard or other place about asynchronous motor behaviour during short-circuit: why consider contribution for maximum short-circuit and not for minimum? during how much time does the motor contribution last during short-circuit? if it stops, why? because it breaks, because it self-stops?