Idealization of Integral Pier

Status
Not open for further replies.

Imran Structural Engineer

Civil/Environmental
Joined
Jun 8, 2021
Messages
28
Location
PK
Currently I'm working on design of bridge with integral pier. Usually, for typical non-integral highway bridges with pile/column bent pier, it is practice at our office to assume K value of 1.2 in bridge's transverse direction and 2.1 in longitudinal direction (AASHTO Table C4.6.2.5-1) when fixed at bottom. However for integral bent type, even though the manually calculated value comes below 1.2, should I safely assume value of K to be 1.2 for both directions?
Thank you.
 
K of 1.2 should be a conservative assumption, but we would typically design that as a frame using a refined analysis (FEM or stiffness matrix), where the K value is not relevant.

Rod Smith, P.E., The artist formerly known as HotRod10
 
@BridgeSmith
Thank You.
I was using K value for the calculation of Euler Buckling load.
 