ICF Walls above 10ft

Status
Not open for further replies.

bdlc2k

Structural
May 6, 2010
26
I have designed a couple of ICF homes with 8-10ft plate height where prescriptive design is allowed. However we are being approached about a commercial building with wall heights of 15-20ft. We are probably going to use flat wall. My question is what ACI method is most commonly used? Empirical design method from ACI 14.5 or Slender wall method from ACI 14.8? Any other input for commercial application is appreciated. Thanks!
 
Replies continue below

Recommended for you

I've done a couple of commercial buildings with walls from 15' to 20' without any problems. I used a slender wall approach (actually the ACI method) and wrote my own interaction diagram programs to calculate the capacities.

The Portland Cement Association has a couple of soft cover books for ICF wall construction.

I did the first (I think) ICF building in Manitoba about 40 years ago using a product called FoamForm. It was a 3 storey 'walk-up' in Dauphin, Manitoba...

Dik
 
Pull the manufacturer's ICC report and follow their recommendations. There are many ways these walls are built (solid core, hollow cells @ 15" o.c....)
 
Different ICF manufacturer's have slightly different configurations...

Dik
 
I have designed 4 story ICF and plank hotels. I typically have to design by Chapter 10 of the ACI 318 since my stress violates any of the chapter 14 methods.
 