Let's look at it step by step.
Under static conditions, an increase in heat transfer rate will mean that the length of the flooded portion of the evaporator will be less. The length of the superheat section will be correspondingly greater. More super heat.
More super heat will tend to open the control valve to restore the superheat to the set point.
Possible result: Greater refrigerant flow, slightly higher back pressure, more BTUs of cooling, more load on the motor.
This may be a quick and economical way to slightly increase the capacity of a system if site conditions indicate that the motor is capable of taking more load. Consider not only normal load but cool down load also.
Comments?
Bill
--------------------
"Why not the best?"