vandede427
Structural
- Aug 13, 2008
- 344
My question is in regards to what information (specifically all the seismic design data listed in IBC 1603.1.5, or the wind info too) do you put in your general notes when doing modifications/alterations to an existing building.
There's the urban revitilization trend where owners buy an old warehouse or an old building and turn it into office space. Also, my office has done several jobs recently where churchs have bought vacant bldgs that were formerly big box retail or theaters and turned them into sanctuaries.
What I'm running into is that the modifications fall under the Alterations Level 2 category of the Existing Building Code (not increasing effective seismice weight by more than 5%). The ICC Existing Bldg code allows the existing lateral system to stay, but the current lateral load resisting system is no longer allowed under new IBC standards.
What do I say in my notes? Do I list the lateraly system as required by 1603.1.5, even though it's not allowed for new bldgs, but give some verbage that the existing code allows it for the existing one?
There's the urban revitilization trend where owners buy an old warehouse or an old building and turn it into office space. Also, my office has done several jobs recently where churchs have bought vacant bldgs that were formerly big box retail or theaters and turned them into sanctuaries.
What I'm running into is that the modifications fall under the Alterations Level 2 category of the Existing Building Code (not increasing effective seismice weight by more than 5%). The ICC Existing Bldg code allows the existing lateral system to stay, but the current lateral load resisting system is no longer allowed under new IBC standards.
What do I say in my notes? Do I list the lateraly system as required by 1603.1.5, even though it's not allowed for new bldgs, but give some verbage that the existing code allows it for the existing one?