KirkGH
Structural
- Jul 17, 2008
- 29
I'm working with a client who had code enforcement tell them their stair handrails needed to be "brought up to code." My interpretation is that any and all modifications need to be made to meet IBC 2009 (current city adopted code). My client thought that just meant adding pickets to create a 4" spacing. I told the client no, the current code says there needs to be a guardrail and handrail. Does anybody agree or disagree with this? As far as I'm reading the code, 1009.12 says plainly handrails are required each side and need to be designed according to 1012. Furthermore 1013.1 says guards are required at stairs and 1013.2 says they need to be 42". This is group R-2 occupancy for exterior public stairs. Therefore the exceptions at 1013.2 do not apply.
Long story short is there is an existing 34" (approximate) steel handrail each side. My plan so far has been to weld on to the existing rail to create a 42" guard and 36" handrail that stays within the 4" allowance per 1012.8.
Feedback is appreciated. Does this all sound correct? I believe I'm interpreting the Code correctly but it's a lot of time and money wasted if I missed something in the Code that could potentially reduce the work. Note that I looked at several developments in my city. One apartment complex just finished has a handrail and a guardrail stair and one development finished a few years ago has a handrail and guardrail. I saw a development today (which got me thinking) that has a handrails with no guard, but later research showed this most likely falls under the 1013.2 exception for interior of R-2 occupancies.
I appreciate your time.
Kirk G Hall, PE
Long story short is there is an existing 34" (approximate) steel handrail each side. My plan so far has been to weld on to the existing rail to create a 42" guard and 36" handrail that stays within the 4" allowance per 1012.8.
Feedback is appreciated. Does this all sound correct? I believe I'm interpreting the Code correctly but it's a lot of time and money wasted if I missed something in the Code that could potentially reduce the work. Note that I looked at several developments in my city. One apartment complex just finished has a handrail and a guardrail stair and one development finished a few years ago has a handrail and guardrail. I saw a development today (which got me thinking) that has a handrails with no guard, but later research showed this most likely falls under the 1013.2 exception for interior of R-2 occupancies.
I appreciate your time.
Kirk G Hall, PE