McCalf
- Apr 4, 2006
- 12
We have a difference of opinion in our office, and I am hoping to get clarification from some other colleagues. IBC 3403.2 permits an increase in gravity load on the existing structure, provided the stresses in the member do not increase by more than 5%. The language varies slightly between IBC 2006, IBC 2009, and IEBC. We are checking existing joists for the weight of a new small mechanical unit. The joist falls within a drifting snow zone that apparently was not considered when the building was designed in 1962.
1. If I ignore the snow drift and check the joist for original loads plus the weight of the unit, the stresses do not increase by more than 5%. At this point, is a reanalysis required?
2. If I include the snow drift, the stresses increase by more than 5%. We exceed the allowable load by approximately 4%. Do we need to reinforce this joist?
3. Hypothetically, if the joist is stressed to 98% of capacity based on existing loads, and I add a mechanical unit that increases the stress to 103% of capacity, is it acceptable? We are not increasing stress by more than 5%, but we have exceeded the allowable load
I think IBC needs address the ambiguity of section 3403.2. Your thoughts?