JAE
Structural
- Jun 27, 2000
- 15,587
Alright - here's the question - In the IBC 2000, there is Chapter 16 that outlines the seismic loads for buildings - these are based on an R value which is based on the type of structure. The end of the Table 1617.6 has a part 7 - "Steel systems no detailed for seismic" - so far so good.
In Chapter 22 (steel) the section 2212.1.1 calls for the use of the AISC Seismic Provisions to be used for SDC A, B or C IF you use any of the R values from Table 1617.6. It then says that IF you use the part 7, "Steel systems no detailed for seismic", you can use R=3 and then NOT use the AISC Seismic Provisions.
I can follow that, too.
Now in the AISC Seismic Provisions, Section 1.0 "Scope" immediately says that, "These Provisions shall apply to buildings that are classified in the Applicable Building Code as Seismic Design Category D and higher..."
So I guess the IBC was written later than the AISC Seismic and inserted the use of SDC A, B and C buildings into it, with the only OUT being the use of R=3.
Do you agree? Thanks for any responses.
In Chapter 22 (steel) the section 2212.1.1 calls for the use of the AISC Seismic Provisions to be used for SDC A, B or C IF you use any of the R values from Table 1617.6. It then says that IF you use the part 7, "Steel systems no detailed for seismic", you can use R=3 and then NOT use the AISC Seismic Provisions.
I can follow that, too.
Now in the AISC Seismic Provisions, Section 1.0 "Scope" immediately says that, "These Provisions shall apply to buildings that are classified in the Applicable Building Code as Seismic Design Category D and higher..."
So I guess the IBC was written later than the AISC Seismic and inserted the use of SDC A, B and C buildings into it, with the only OUT being the use of R=3.
Do you agree? Thanks for any responses.