Hi there.
I got a disconnector switch with short current rated to 31,5KA/1s, I need to demonstrate that his contact are able to support 31,5kA/3s. Based on type tests recorded earlier, the only information I have are the contact resistance and contact area, can anybody give me a tip if it is possible to "SIMULATE" this extra thermal stress? I really don´t think that i²T is saying anything about this extra contact thermal efforts.
Best regards;
Manoel.
I got a disconnector switch with short current rated to 31,5KA/1s, I need to demonstrate that his contact are able to support 31,5kA/3s. Based on type tests recorded earlier, the only information I have are the contact resistance and contact area, can anybody give me a tip if it is possible to "SIMULATE" this extra thermal stress? I really don´t think that i²T is saying anything about this extra contact thermal efforts.