1. is this a wet system or pre action???
NOOOOOOOOO
24.2 Acceptance Requirements.
24.2.1* Hydrostatic Tests.
24.2.1.1 Unless permitted by 24.2.1.2 through 24.2.1.6, all piping and attached appurtenances subjected to system working pressure shall be hydrostatically tested at 200 psi (13.8 bar) and shall maintain that pressure without loss for 2 hours.
24.2.1.2 Portions of systems normally subjected to system working pressures in excess of 150 psi (10.4 bar) shall be tested as described in 24.2.1.1, at a pressure of 50 psi (3.5 bar) in excess of system working pressure.
24.2.1.3 Where cold weather will not permit testing with water, an interim air test shall be permitted to be conducted as described in 24.2.2. This provision shall not remove or replace the requirement for conducting the hydrostatic test as described in 24.2.1.1.
24.2.1.4 Modifications affecting 20 or fewer sprinklers shall not require testing in excess of system working pressure.
24.2.1.5 Where addition or modification is made to an existing system affecting more than 20 sprinklers, the new portion shall be isolated and tested at not less than 200 psi (13.8 bar) for 2 hours.
24.2.1.6 Modifications that cannot be isolated, such as relocated drops, shall not require testing in excess of system working pressure.
24.2.1.7 Loss shall be determined by a drop in gauge pressure or visual leakage.
24.2.1.8 The test pressure shall be read from a gauge located at the low elevation point of the system or portion being tested.