Although at first, it may be difficult to fathom hydrostatic uplift pressure exceeding dead load of 9-story building with mat slab, it can happen.....and must be considered.
Analysis below is for non-factored loads.
Interestingly, Commentary to ASCE 7-05 and ASCE 7-10 does not address hydrostatic uplift directly.
For ASCE 7-05........load due to hydrostatic pressure was included "out front" in load combinations
Load Combination 7 (ASD): 0.6 DL + Wind + Hydrostatic
When using the 60-percent DL factor......there has always been question as to whether is should apply to full design dead load used for gravity load design or to actual weight (which is generally less and perhaps much less).
For ASCE 7-10.......hydrostatic load (H) is now added to any load combination as noted in "Exceptions".........and can easily cause confusion if not carefully considered.
For uplift condition, my interpretation of these ASCE 7-10 code provisions is that full dead load may be used along with hydrostatic load. However, I submit that dead load used must only be actual weight, not the greater-than-actual weight most often used for gravity load design.
Using ASCE 7-05......with full design DL.......4-inch thick concrete slab on steel deck (40 psf) plus steel framing (10 psf) plus partition walls (10 psf to be conservative).......and neglecting weight of roof.......uniform dead load for 9 floors is 540 psf. For 2-foot thick slab, weight of slab is 300 psf. For this rough estimate, weight of foundation walls is also not included.
Per ASCE 7-05; usng 60-percent DL factor for load combinations.....total effective weight is then about 500 psf so that height of unbalanced water would have to be just more than 8 feet to cause net uplift, without taking into account any frictional resistance along sides of basement foundation walls.
This also is based on soil-supported slab (not pile-supported) since slab could be tied to piles to provide much greater uplift resistance.
Net upward pressure against slab underside of slab (at 500 psf) results in net upward pressure of 200 psf for design of slab between columns and foundation walls.
Using ASCE 7-10.........and somewhat lesser DL of 55 psf.......uniform DL is 495 psf. With same 300 psf for slab, height of unbalanced water would have to be 12.8 feet to cause net uplift greater than 795 psf dead load. Net uplift against underside of slab is then 495 psf, much greater than for ASCE 7-05, due to much greater height of unbalanced water.
Of course, lateral hydrostatic pressure must also be considered against foundation walls.
Relief pipes / valves might be one way to limit height of unbalanced groundwater.....as long as basement can safely be flooded (and then drained afterwards!)
Per ASCE 7-05.......wind was clearly to be considered along with hydrostatic load. This does not change with ASCE 7-10 since H-load is to be added to each load combination as applicable. Considering overturning force due to wind against 9-story building........without large effective dead load resistance from building........is rather frightening!
Therefore.......unbalance height of water would almost certainly have to be much less than the height that would equal weight of building.
John F Mann, PE