I do not know of anything in NFPA for the pressure range of "test guages", but according to NFPA-13 2002 edition, 8.16.3.3 the required pressure guages shall be listed and shall have a maximum limit not less than twice the normal system working pressure at the point where installed.
I always use a 300 psi guage like the ones that are on the system riser. Does not sound too safe using a 200 psi guage for a 200 psi test.
When they do their hydro test check the guages on the riser if the piping is connected to the riser.
Hope this helps.