Our cycle is: Condenser Pump - Heater 1, 2,3- Dearetor- Feed Water Pump -Heater 5, 6 , 7 - Boiler. Our inyection of hidrazine is regularly after the condensate pump (which is proportional to the condensate flow in auto), we check the concentration after the Dearetor and before the Boiler. We got some bad experience at begin, we preservate the boiler whit water with hidrazine at 170 ppm, but in the starts all the hidrazine desapear by the high temperature, at 315°C begins his descomposition resulting high values of hidrogen in the steam (experimental data). Actually we are controlling 25 ppb in feedwater before the boiler.
I hope that it can help you.