A 0.50 caliber bullet masses 620 gm and travels at 887 m/s, it takes 9E-7 seconds to traverse a piece of 0.8 mm steel and it has a momentum of 550 N-s.
If you threw a 60 kg mass at 9 m/s you would get the same momentum, but instead of penetrating the steel it would just dent the hell out it.
Same momentum, about the same total force, much longer duration. Duration really matters.
Same thing happens with pressurisation/depressurization. Going from 0 to 315 bar in 32 seconds is a really good way to turn a fabrication into scrap metal. If you give the elastic properties of the metal enough time to equilibrate, you'll get a test that means something. If you don't, then places of localized stresses will reach a peak stress and not be able to transfer the stresses to adjacent pipe and can just come apart.
Whoever wrote that you could go up at 10 bar/s and down at 5 bar/s is making a silly and very dangerous mistake. My guess is that he took a U.S. procedure that said you should go up at 10 psi/s (which is common, if not very conservative) and down at 5 psi/s and "converted" it to metric by replacing psi with bar. Just for reference, 10 psi/s would get you to 315 bar in about 8 minutes. That is REALLY fast. For a liquid test I usually use 50 psi/min (3.4 bar/min) with a 15 minute soak every 1,000 psi (69 bar). To get to 315 bar, I would take 90 minutes of active pressurization plus 15 minutes soak time every 69 bar (total 2.5 hours, not 32 seconds).
David Simpson, PE
MuleShoe Engineering
"It is always a poor idea to ask your Bridge Club for medical advice or a collection of geek engineers for legal advice"