We are considering an air conditioning air distribution control strategy as follows:
1) VAV boxes in some zones are being proposed to regulate the air flow and zone temperature.
2) Other zones will have no control damper. No damper or VAV boxes to regulate the air flow. It is expected that air flow will remain constant after system balancing.
3) The floor which comprises several zones is served by a chilled water central station air handling unit with variable frequency drive.
4) Static pressure sensor will be installed in the air conditioning ducting.
5) The required control hardware will be fitted and programmed (PID loop).
My colleague describes this as a hybrid system and said it will not work as more air will be forced through the diffusers that have no upstream actuator or VAV boxes. I thought that as the VAV dampers in some of the zones close, the static pressure in the duct will increase and the sensor and control system will detect this and signal speed reduction of the fan via the VFD; restoring the static pressure to the original setpoint.
Does anyone have any comment on this? Can you direct me to literature on advanced air conditioning control strategies?
1) VAV boxes in some zones are being proposed to regulate the air flow and zone temperature.
2) Other zones will have no control damper. No damper or VAV boxes to regulate the air flow. It is expected that air flow will remain constant after system balancing.
3) The floor which comprises several zones is served by a chilled water central station air handling unit with variable frequency drive.
4) Static pressure sensor will be installed in the air conditioning ducting.
5) The required control hardware will be fitted and programmed (PID loop).
My colleague describes this as a hybrid system and said it will not work as more air will be forced through the diffusers that have no upstream actuator or VAV boxes. I thought that as the VAV dampers in some of the zones close, the static pressure in the duct will increase and the sensor and control system will detect this and signal speed reduction of the fan via the VFD; restoring the static pressure to the original setpoint.
Does anyone have any comment on this? Can you direct me to literature on advanced air conditioning control strategies?