HX fouling monitoring

Status
Not open for further replies.

pekos

Mechanical
Mar 15, 2005
12
I need to implement a monitoring of HX fouling and I need help to define parameters to control: LMTD?
thanx in advance
 
Replies continue below

Recommended for you

I typically calculate the Uo and watch that. It's not perfect since changing flow rates or physical property changes will also affect the individual heat transfer coefficients but it's easy.

The LTMD is going to increase as you increase the flow rate through one side (for example) though that doesn't mean the exchanger is fouled.
 
Depending on the particular service, sometimes a complete heat balance, coupled with pressure drop measurements may be helpful.
 
with pressure information, it would be easier, but I only have local pressure indicators, for temperature I have more information since it s implemented on DCS
 

Since this would apparently be an intermittent operation, it wouldn't harm the process engineer to visit the site once in a while to take some readings. Do you agree ? [smile]
 
I totaly agree for the engineer monitoring level, but we intend to implement indicators on PI for managers, with alarms levels..., to make them see the $losses
 