sapark/pete,
From 6.6 KV wye to 3.3 KV delta, the phase voltage is down by 15% and the starting torque is down by square of 3.3/3.8. We do not the motor application where such a reduced torque could result in stalling. Also, if the motor runs at rated load (315 KW), the running current will be higher by 15% which may heat up the winding. Due to these reasons, my post. From insulation point, no problem.
Kumar