We have an exterior stair column (HSS 3x3x1/4) with a K-brace that was field-welded mid-height. The 2 diagonal brace members are L3x3x1/4, welded to the column with 1/4" fillet welds all-around. The column is 11.5 ft tall. The owner noted that it appeared the column had been hit and was deflected. Contractor verified that column is deflected 7/16" (l/315) but states that it is due to the field-welded brace connection. The deflection is perpendicular to the plane of the brace. A couple of basic questions come to mind:
- Is the erection tolerance of l/1000 what controls? If so, then this column is out of tolerance.
- The column is relatively lightly loaded (4,000 lb max) so being out-of-plumb by 7/16" isn't as much of a structural concern. However the owner's a bit annoyed that the contractor didn't point it out first.
- Could field-welding braces on cause this type of deflection? Thoughts on how to prevent it in the future? Is this up to the erector to provide adequate temporary bracing if needed to counteract effects of welding deformation?
Thanks for any insight.