Hello, sorry for late reply. I'm sharing the oscillographic records here. This is a cable + OHL line. The line is three terminal line but protected from only two terminals with cable differential relay. Because there is no generation on the third terminal. So the current flows to the third terminal is not known by the relays on other terminals. The differential current threshold is set 600 A so the relays will not operate during load conditions. (400 kV line , 125+125 MVA installed power on the third terminal ) In fact, this was a relay misoperation due to improper setting because only the load conditions was considered on the third terminal but fault conditions should've been considered too. On the other hand, I thought there was a fault on the low voltage side of the third terminal substation and it was seen as a differential current by relays on other terminals. But when I ask them if there was any fault in the low voltage side of the third terminal substation, they told me there wasn't. And I don't get it how this happened. There is an electric arc furnace on the third terminal substation. Is there any possibility that the load side caused some kind of transient overcurrent with a vector diagram like that?