So, we have no humidifier, but do we have a reheat coil or the means to reheat with the primary heating coil? If the heating coil is not downstream of the cooling coil, then presumably, we don't have reheat capabilities. If not, then I guess the humidistat is "wired in parallel" like a former respondent said, but all it can do is allow the cooling coil (and compressor and fans, etc.) to remain on for a longer period of time if humidity conditions are not satisfied. This will begin to "sub-cool" the space, so I guess the idea is not to set the humidistat too low.