In additional to OldFieldGuy and Eleceng01 posts, I would like add: 22574, don't learn testing of relay SEL121G, learn test protective functions. Don't learn Double F6150( BTW according to my partners is excellent tester), learn what you need inject for right relay operation and don't inject Z---> please inject U and I and phase angle between.
Regards and Good Luck.
Slava...
COMPLETELY IN AGREEMENT.
GOOD POST SLAVAG!
A fault is represented by voltages and currents. NOT impedance. Automatic test plans are not good to understand the relays.
And then again.... we can go to my old post: what does TEST mean?
I am fully convinced that:
- Commissioning/routine tests of the relays must be done according to recommendation in relay manufacturer, and NOT acording recommendations of relay test sets. Only the manufacturer knows how the relay works, and only the manufacturer can tell you how to test it in order to understand that it is working fine.
-Performance tests can be done "as you want", not considering how the relay works. But then you must make sure that your tests are realistic tests, because if somenthing doesn't work, you must be able to give a good and significative report to the manufactuer without that you imply 3 persons working for you to discover you are testing the relay OUTSIDE of its application, which is protection of power systems and not just response to some currents and voltages. Testing the characteristic, is not a performance test.