Allen-Bradley has a "Bulletin 1336 Adjustable Frequency AC Drive Troubleshooting Guide and Renewal Parts" manual that may be helpful. This has some trouble-shooting hints, including how to test their IGBT's. It also has simple block diagram schematic for the 3-30HP and 5-52HP models, and parts lists. I think it may be downloadable on their website.
Reflected waves can also cause high voltage spikes at the motor end, and can break-down the motor wire insulation, especially if the motor isn't wound with spike-resistant wire. With 400 feet of wire, a load-side reactor should certainly be considered. Mount this as close to the drive as is reasonable.
Other causes could be line-side voltage problems, especially single-phasing problems if the drive is big enough. The filter caps on some bigger drives don't smooth out the ripple you get with single-phasing conditions, and if it is trying to run near full load, you get a lot of excess heating on the lower-end.
If you do find a bad IGBT module, and you still want to repair the drive, I suggest replacing all three of the modules, and checking out the caps and bridge as well. I'm just a service tech, but past experience has shown me that you get better results changing all the modules.