I have never sized vents before, and am asked to confirm slop oil tanks (quantity -2) vent sizings for inter-tank transfer as well as in-flow from upstream sources. The tanks are 45' ID by 35' high. DP is 2.5" water int. & 1.24" water ext. at -50 F. The current vent sizes are 12 x 14" at +/- 0.5 oz. There are 2 vents per tank.
I've looked at the API std. 2000; but I'm confused as to how it'll tell me about vent sizes. Based on the data sheet, the oil movement in/out is 240,000/120,000 gph respectively. I've calculated the breathing required for oil movement to be 16000 scfh air in and 68571 scfh air out. The thermal breathing required was found from the tables to be both 10,000 scfh air in/out. How exactly do I go about ensuring that 12 x 14" is adequate size for a vent? I've tried to speak to the vendor to no avail. What exactly should I go about doing?
I've looked at the API std. 2000; but I'm confused as to how it'll tell me about vent sizes. Based on the data sheet, the oil movement in/out is 240,000/120,000 gph respectively. I've calculated the breathing required for oil movement to be 16000 scfh air in and 68571 scfh air out. The thermal breathing required was found from the tables to be both 10,000 scfh air in/out. How exactly do I go about ensuring that 12 x 14" is adequate size for a vent? I've tried to speak to the vendor to no avail. What exactly should I go about doing?