A little late in responding due to other commitment. In dry storage the boiler should have been thoroughly dry and afterward trays of dessicant such as quicklime or silica gel placed in the steam and water drums. All connections should be tight, valves closed, handholes and manholes closed for the duration of storage. An alternate method is to have either a circulation of dry air or the introduction of an inert gas pressurized in the boiler.
I agree with StoneCold with the surface rust appearance which you can maintain as is with the procedures outlined above until such time that the boiler is ready for startup, then the chemical treatment should be able to remove that surface rust.
About the fireside, how did it look?