Mmmmm... I noticed I've buggered up this solution :-(
To calculate sensible load, we need to establish change in enthalpy at constant humidity ratio, therefore, at 62°F dry bulb and humidity ratio = 0.01067:
enthalpy = 26.52 Btu/lb
m
Sensible load then becomes:
28.8 (31.43 - 26.52) = 141.4 Btu/min = 0.707 tons
Total load is solved using the conservation of energy equation:
m
a * h
1 = m
a * h
2 + m
w * h
w + q
where:
m
a = mass flow of dry air
h
1 = return air enthalpy
h
2 = supply air enthalpy
m
w = mass of water removed
h
w = enthalpy to condense water
q = total load
And the conservation of mass equation:
m
a * W
1 = m
a * W
2 + m
w
where:
m
a = mass flow of dry air
W
1 = return air humidity ratio
W
2 = supply air humidity ratio
m
w = mass of water removed
Combining these equations, we get:
q = m
a * (h
1 - h
2) - m
a * h
w * (W
1 - W
2)
Using the above equation, and the numbers established in the previous post, we get:
Total cooling load: 0.985 - 0.009 = 0.976 tons
and not: 0.985 + 0.009 = 0.994 tons
The latent load becomes: 0.976 - 0.707 = 0.269 tons
Hopefully, I did not confuse the point I was trying to make...