I agree with davidbeach. It will be more likely that the transformer has been wound with copper instead of aluminium. Usually welding transformers consist of aluminium windings. Big distribution transformers have Cu. I have never heard of 2MVA transformer to have aluminium. I work for a transformer company where I design transformers and power supplies.
My question is why do you need to know what material was used to wind the transformer.
If you want to know if it has been wound with copper or aluminium you can try and calculate it by working out the resistance of the winding.
Formula: R= pL/A
Where R= resistance/metre , p=resistivity (ohm m),L= length in m, A= cross sectional area.
p for Copper = 1.68 x 10^-8
p for Aluminium = 2.65 x 10^-8
Therefore if it is aluminium the resistance will be greater. You will have to estimate/calculate mean turn of a coil to get yout L (total length in meteres) and you should calculate this fairly easy.
Hope this helps.