bacon4life
- Feb 4, 2004
- 1,531
We recently had a 7000 amp line ground fault one feeder that also caused an adjacent feeder to trip on about 1500 amps of 3I0 current (500 amps on each phase). One possible cause would be grounded wye-delta connected transformer bank somewhere on the adjacent feeder. Other than inspecting every transformer on the feeder, are there any other ways to identify which portion of the feeder might have the incorrectly connected transformer bank? Or are there other ways for ground fault current to show up on the phase conductors of an different circuit. This is a 12 kV grounded wye distribution system.
Feeder 4 fault currents:
A-7000 <0 degrees
B-0
C-0
Feeder 1 fault currents:
A-500 <180 degrees
B-500 <180 degrees
C-500 <180 degrees
A-7000 <0 degrees
B-0
C-0
A-500 <180 degrees
B-500 <180 degrees
C-500 <180 degrees