llc0612:
First off, I don't believe there is any API recommended practice or "code" to go by or go to. I have used the engineering criteria pertinent to the process. In other words, you require thorough knowledge of the process and it's capabilities and, knowing these, you apply logical and safe criteria to each specific alarm or shutdown activation.
For example, the LAHH (Level Alarm, High-High) is usually the "last resort" prior to an emergency shutdown of the unit in question. Taking this into consideration, I always try to allow for sufficient, safe operational time to take the necessary steps to avoid the ultimate shutdown and employ an alternative plan. This involves expert instrumentation knowledge of the speed and response involved with the instruments being used as well as the maximum flowrates of fluid entering the subject vessel. Other details may enter into the logic employed - such as vessel location and type of vessel and fluids involved.
In my process design I always insist on a detailed and specific explanation of the set points for each alarm and shutdown point. These are reviewed and scrutinized in detail at the preliminary design, the final design, and certainly at the HazOp phase. I am accustomed to running at least 2 or 3 HazOps prior to the actual commissioning, so these points are discussed redundently.
In my opinion this is a very good and important question that often is not given the priority and serious attention that it deserves. I personally feel that all involved engineers should press and demand clear and accurate explanations of these functions from the responsible process engineer(s) - not from the instrumentation engineers, who unfortunately are usually kept in the dark regarding process characteristics.
I am interested in reading what other forum members have to say about this important subject.
Art Montemayor
Spring, TX