This is a puzzle for me, I have some Ideas, but I could use some more ideas.
---------------
Problem:
Test a 4160 Volt NEMA G motor/pump combination on a skid, given a 480 Volt source.
---------------
Things I have:
I have a 480 Volt source, with a 400 Amp circuit breaker.
I also have a 500kVA transformer that I can use to step up the voltage to 4160 Volts. (4160/Y480)
I have a 4160 Volt, 150 HP motor connected to a pump.
I have the pump connected to water that the pump will move to test the motor/pump skid
---------------
This is what I think I know:
1. The motor will take 10 to 15 seconds to spin up to 1760 rpm.
2. The draw for the motor during startup will be up to 120 Amps (19.1 full load Amps * NEMA G ~6.2 times), this is about 170% of the transformer FLA, and will require over 1000 Amps at the 480 Volt source.
3. Because of 1. and 2. above, and the inrush on the transformer, I am sure the 400 Amp circuit breaker cannot be used to close into a circuit containing only the step-up transformer and the motor.
4. The basic circuit will go something like this:
-480 Volt, 400 Amp circuit breaker
-Cable
-4160/480V 500kVA transformer
-Cable
-4160 Volt 150HP motor
---------------
My solutions:
Solution 1.
Put a current limiting drive on the 4160 Volt portion of the circuit between the transformer and the motor. This would limit current on the motor to 2 or 3 times the FLA of the motor until it is up to speed. The FLA of the motor is 19.1 Amps at 4160 Volts. I calculate that would require 166 Amps on the 480 Volts side of the transformer. If the drive can limit current to 38.2 Amps, then the 480 Volt side would only need 332 Amps.
My problem with this solution is that the drive is expensive, hard to find, and this setup is a onetime test, we will never do it again. What will I do with the drive when I am done.
Solution 2.
Put a current limiting drive on the 480 Volt side of the transformer. If I can limit current to under 400 Amps on the 480 Volt side of the transformer, maybe I can start the motor and the transformer at the same time. A 480 Volt drive is easy to find, and we can sell it when I am done with it.
My problem with this solution is that I don't trust myself. I can model inrush and motor start up current, but I am not a drive expert. I have no idea what kind of drive will do this. I am thinking that a VFD will not do the job. This is where I think I need help, but I could be totally wrong, and in need of help with the whole solution.
Solution 3.
I can add a 800 Amp circuit breaker to the 480 Volt panel. 800 Amps is the limit of the panel. This may make one of the solutions above more feasible.
Solution 4.
Some smart engineer on the internet tells me the right answer. At first this looked like an easy problem to me. I sketched the circuit, did some quick calculations, and said we will do this. Then I looked closer and said we need more parts. And now, I am asking for help.
What say you???
---------------
Problem:
Test a 4160 Volt NEMA G motor/pump combination on a skid, given a 480 Volt source.
---------------
Things I have:
I have a 480 Volt source, with a 400 Amp circuit breaker.
I also have a 500kVA transformer that I can use to step up the voltage to 4160 Volts. (4160/Y480)
I have a 4160 Volt, 150 HP motor connected to a pump.
I have the pump connected to water that the pump will move to test the motor/pump skid
---------------
This is what I think I know:
1. The motor will take 10 to 15 seconds to spin up to 1760 rpm.
2. The draw for the motor during startup will be up to 120 Amps (19.1 full load Amps * NEMA G ~6.2 times), this is about 170% of the transformer FLA, and will require over 1000 Amps at the 480 Volt source.
3. Because of 1. and 2. above, and the inrush on the transformer, I am sure the 400 Amp circuit breaker cannot be used to close into a circuit containing only the step-up transformer and the motor.
4. The basic circuit will go something like this:
-480 Volt, 400 Amp circuit breaker
-Cable
-4160/480V 500kVA transformer
-Cable
-4160 Volt 150HP motor
---------------
My solutions:
Solution 1.
Put a current limiting drive on the 4160 Volt portion of the circuit between the transformer and the motor. This would limit current on the motor to 2 or 3 times the FLA of the motor until it is up to speed. The FLA of the motor is 19.1 Amps at 4160 Volts. I calculate that would require 166 Amps on the 480 Volts side of the transformer. If the drive can limit current to 38.2 Amps, then the 480 Volt side would only need 332 Amps.
My problem with this solution is that the drive is expensive, hard to find, and this setup is a onetime test, we will never do it again. What will I do with the drive when I am done.
Solution 2.
Put a current limiting drive on the 480 Volt side of the transformer. If I can limit current to under 400 Amps on the 480 Volt side of the transformer, maybe I can start the motor and the transformer at the same time. A 480 Volt drive is easy to find, and we can sell it when I am done with it.
My problem with this solution is that I don't trust myself. I can model inrush and motor start up current, but I am not a drive expert. I have no idea what kind of drive will do this. I am thinking that a VFD will not do the job. This is where I think I need help, but I could be totally wrong, and in need of help with the whole solution.
Solution 3.
I can add a 800 Amp circuit breaker to the 480 Volt panel. 800 Amps is the limit of the panel. This may make one of the solutions above more feasible.
Solution 4.
Some smart engineer on the internet tells me the right answer. At first this looked like an easy problem to me. I sketched the circuit, did some quick calculations, and said we will do this. Then I looked closer and said we need more parts. And now, I am asking for help.
What say you???