Waross, %impedance is same from primary side or secondary side or step down or step up.
With open delta auto connection, the rating kVA to line output ratio = 1.15 (E1-E2)/ E1 =0.23, in this case. ie out put in this case will be 2x50x0.23 = 86.6 kVA. Based on this, I 'gusstimate' the line impedance as 1.1 % on 86.6 KVA.
Geometrical neutrals of the HV and LV circuits will not coincide. A difference in voltage exists between them at fundamental frequency,equal to 0.57(E1-E2) = 68.4 V ,in this case. Hence it is possible to ground the neutral of only one circuit,but not both. If both neutrals are grounded, a low impedance path for the neutral displacement voltage results,leading to a single phase short circuit current to flow through the entire length of the system,returning through the ground connections,(ref Transformer Engineering (book) - L F Blume.)