Ben29:
There will still be trust to the ext. bearing walls to the extent that the rafters settle in their hangers or the ridge beam deflects, just imagine the geometry, the rafters don’t shorten. And, don’t make a full width/long horiz. seat cut on the rafter at the top of the wall, that is no better. You are still applying the bearing load in a way which imparts cross grain tension to the top half of the rafter, at about mid depth. Archs. do all kinds of crazy things becuase their pencils tell them to do it or their CAD programs make them do it, they have no real sound reasons, they need to fill the space with something. You have to be a bit of an educator and gently explain the errors of their ways. I would lower the double top plate to provide the 1.5" deep birds mouth on the rafter and then apply something akin to a 2x10 (2x8?) rim joist out at the outer face of the stud wall, bevel ripped on the top to match the roof SIPS. I would run the wall SIP’s up to within 1.5" of the underside of the gutter, and install a single 2x member on top of the SIPS to tie them all together, and eliminate the three 2x blocking members at the top of that wall section. You better be very confident in your gutter installer’s capabilities or you could be growing mushrooms in those walls.