Logikman,
I agree with BJC on this'n. The switches you identified are probably both good for your load, but they really should have a specific "ballast" rating like lighting contactors and mainstream snap-type toggle switches.
Inrush to a ballast can be anywhere from 1.5X to 10X steady state, depending on type, age, etc... You'd need info from both the ballast manufacturer (for the specific ballast you want to use) and the switch manufacturer if it doesn't carry a true ballast rating.
Again, based on what you're telling us (4 or 5 luminaires, each probably about 1 amp maximum steady-state, your switches you found are probably good for the task. Using the low-voltage plus relay solution is a lot slicker though.
Let us know what you wind up trying!
Old Dave