stanier brings up and pushes a great issue.
I read a "technical" paper by an air vent manufacturer about four years ago. Follow their advice and your system will look like it has warts growing all over it for the number of valves they recommend, and their approach is ....
Just to be sure, Just in case, something like that.
I have decided to address each system diligently, and put in the valves needed, and not to just "make sure" or "just in case".
If velocities ever exceed some value, say about 2 feet per second, the air is swept onwards, depending on slope and fluid type.
If the fluid is saturated or near saturated with dissolved gas/air, that is a problem, especially if temperatures drop.
Why not be careful in the design? It seems silly to start specifying hundreds of warts on the pipe, that gets engineers a bad name quick, especially after someone goes around plugging them up cussing the guys that specified them, because those people know why the engineer did it, "Just to be Safe".
I have to say this however, I have never seen any engineer give in on this, it is like superstitions, they have no valid reason other than it makes them feel good.
PUMPDESIGNER