electricpete
I am interested in how a 2-speed 1-winding consequent pole motor accomplishes change in speed. (not how it is wired to accomplish the various constant horsepower, constant torque etc connections).
Here is some discussion of the principle of a consequent pole motor.
So it’s clear the high speed winding is typical winding construction.
For example if we look at the pole phase groups moving around the circumference for a 4-pole motor, 60hz motor (1800rpm) we might have something like:
A, B’, C, A’, B, C’ A, B’, C, A’, B, C’
Now to get to slow speed (900rpm), something strange is required. The poles in the slow speed diagram are arranged as follows:
A B C A B C A B C A B C
It makes perfect sense to me that this slow speed arrangement yields 900rpm = half the speed of the high speed connection, but not for the reasons stated in the quote above.
I don’t understand the need for any “induced poles” to accomplish this... in my mind it is simply a re-definition of what constitutes a pole (or more specifically the time interval between poles). There is no need for another pole between ppg A and ppg B to provide return path for flux, because A and B have different phase. And their discussion of induced pole implies a return path involving through the frame involving homopolar flux (“The core and frame must be made from a special high permiability steel to provide the flux path for these virtual poles”) – I don’t see the need for that: the fluxes from A+B+C sum to 0 in the same way that the fluxes from A+B’+C+A’+B+C’ sum to 0. If one were of the opinion that the flux from A must return through A’, then one would conclude that an induced pole is necessary. However imo there is no reason the flux from A cannot return thru B and C.
To my way of thinking:
#1 - the high-speed (typical) pattern A, B’, C, A’, B, C’ A, B’, C, A’, B, C’ has 60 electrical degrees between pole phase groups. So for the field to go once around the stator = 12 pole phase groups will require 12*60 degrees = 720 degrees = 2 cycles = (2/60) sec = (1/30) sec => 1800rpm.
#2 - the low-speed pattern A, B, C, A, B, C A, B, C, A, B, C has 120 electrical degrees between pole phase groups. So for the field to go once around the stator = 12 pole phase groups will require 12*120 degrees = 1440 degrees = 4 cycles = (4/60) sec = (1/15) sec => 900rpm.
What is your opinion? Did we add 4 more poles to the 4-pole motor in converting from fast to slow as they suggest above? Or did we simply move the existing 4 poles farther apart in time as described above #1, #2?
Is there a homopolar flux path required for a consequent pole motor as they suggest? Or not (as per my analysis).
Also I can see that overlap between phases would significantly degrade the winding factors in the slow speed application unless coil span were adjusted. Is coil span typically a smaller fraction of pole span for consequent pole motors than others?
uiitraining said:Each type of consequent pole motor winding will have two separate connections. One is for the high-speed number of poles (4, 6, etc.) and one is for the low-speed number of poles (8, 12, etc.). A specially designed motor controller is used to supply power to the connections (speed) desired. The poles in the high-speed connection will be connected for alternate polarities. Poles in the low-speed connection will be connected for the same polarity, and an equal number of poles of opposite polarity will result as a consequence. That is, the opposing same poles flux create a virtual opposite pole between them. The name consequent pole comes from this consequence. The core and frame must be made from a special high permiability steel to provide the flux path for these virtual poles.