Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

How do you correctly calculate the heat transfer load?

Status
Not open for further replies.

Wally89

Industrial
Joined
Feb 24, 2020
Messages
2
Location
IT
I'm trying to determine the heat transfer load of a sealed cabinet I'm a bit confused about the formula that is apparently used for it. I would appreciate some help. The formula is:

(q = (To - Ti ) ÷ [(1/ho ) + (1/hi ) + R] x 5.67

Definition of Variables— q = Heat transfer load per unit of surface area To = Maximum ambient temperature outside the enclosure Ti = Maximum rated temperature of the electrical components ho = Convective heat transfer coefficient outside the cabinet Still air: h = 1.6 Relatively calm day: h = 2.5 Windy day (approx. 15 mph): h = 6.0 hi = Convective heat transfer coefficient inside the cabinet Still air: h = 1.6 Moderate air movement: h = 2.0 Blower (approx. 8 ft.3/sec.): h = 3.0 R = Value of insulation lining the interior of the enclosure walls No insulation: R = 0.0 1/2 in. or 12 mm: R = 2.0 1 in. or 25 mm: R = 4.0 1-1/2 in. or 38 mm: R = 6.0 2 in. or 51 mm: R = 8.0
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top