Below is the hose description
Elastomeric lining, Synthetic fibre reinforcement and elastomeric coating on the reinforcement.
with diameter 3 inch
and length 30m
thanks
Search for the NFPA document "determination of fire hose friction loss characteristics"
The fire fighting industry uses a slightly different approach to calculating pressure drops from that used by process and mechanical engineers. I re-jigged the data from page C-6 of the referenced article to work out that the average roughnesses were between 0.02 and 0.05 mm. For typical fire hose sizes this variation makes very little difference to the calculated pressure drop and for my AioFlo program I have used 0.05 mm.
Note that these values do not apply to spiral reinforced hoses which have a bellows like internal surface.
The equation you found for hl is what is known as the Darcy-Weisbach equation. The equation shown on the Fire Engine Academy page is a simplified specific version of the Hazen-Williams Equation. The Darcy-Weisbach equation is generally regarded as a more accurate and versatile equation, but if you are working with water and you have the correct Friction Loss Coefficients the Hazen-Williams is acceptably accurate.
Because Hazen-Williams is easier to use, and has been around longer, it seems to be the equation recommended (or even mandated) by fire protection authorites world-wide. I don't do a lot of fire water work, but when I do I use Darcy-Weisbach to be sure that I have got the correct pipe sizes or flow rates, and then I re-run the calcs with Hazen-Williams to satisfy the authorities.