Noncurrent-Carrying Items
Many times other problems can be spotted with ancillary
items which normally do not carry current and, therefore,
(mistakenly) are not part of the normal infrared survey.
Thermographers, experienced in the vastness of potential
problems, will many times glance around in their field of
view and spot other items radiating heat (or not radiating
heat), which will raise their curiosity level to the point of a
closer look. Many times a metallic structural support, cableway,
or cable tray assembly, none of which should be car-
rying current, will indicate heating that is apparently from
electrical current flowing. Field measurements of hundreds
of amperes have been seen numerous times and are most
commonly the result of excessive eddy currents caused by
inductive heating. This heating effect can cause the surface
temperature to rise well beyond the boiling point of water,
potentially presenting a burn hazard to personnel or the
deterioration of other substances in close proximity.
Grounding connections normally do not carry continuous
current; therefore, a ground connection showing any increase
in temperature can indicate a possible problem. Further
investigations of these types of problems have uncovered a
variety of issues, such as ground loops, broken or disconnected
grounds, and high impedance faults.