Jun 7, 2016 #1 KLH Mechanical Joined Jan 25, 2002 Messages 75 Location US Hello all, Does anyone know why Figure A.7.3.2(d) in Annex A of NFPA 14 2007 shows two hose valves? Paragraph 7.3.2 doesn't require two valves. Later editions only show one hose valve but here in PA we follow the 2007 edition. Thanks, Ken
Hello all, Does anyone know why Figure A.7.3.2(d) in Annex A of NFPA 14 2007 shows two hose valves? Paragraph 7.3.2 doesn't require two valves. Later editions only show one hose valve but here in PA we follow the 2007 edition. Thanks, Ken
Jun 7, 2016 Thread starter #2 KLH Mechanical Joined Jan 25, 2002 Messages 75 Location US Maybe for testing the most remote standpipe??? Other standpipes would just have one? Upvote 0 Downvote
Jun 7, 2016 #3 cdafd Specifier/Regulator Joined Aug 18, 2005 Messages 2,953 Location US 500 gpm ? Upvote 0 Downvote
Jun 7, 2016 #4 TravisMack Mechanical Joined Sep 15, 2003 Messages 1,777 Location US Yes..testing as others have said. Getting the 500 gpm. Travis Mack MFP Design, LLC http://www.mfpdesign.com"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Upvote 0 Downvote