Thanks y'all.
fatdad, so say I have a 20' cantilever wall.
1) Is this movement measured at the same location of the developing pressures? E.g. Let's say it's 1"/10' to develop passive pressures. At 15' up the wall, I'll need 1.5" of deflection towards the backfill at that location for passive pressures to develop? What about at the very bottom of the wall (z=0)? I theoretically need 0" of deflection for passives? Or is it that the top of the wall needs to maximize deflection (2" in this example) before passive pressures can be considered anywhere?
2) In my particular case, where I'm designing for a loading scenario towards the backfill, I will never have active pressures. Active pressures only develop when a wall moves away from the soil, not towards. So unless I'm willing to allow the passive deflections, I should use at-rest pressures?
3) If I model this thing with at-rest pressures return deflection values in excess of the 1"/10' rule, that means my model is no good and I need to reiterate using passive pressures? Conversely, that model using passive pressures should show at least 1"/10' deflections to be considered valid, right?
4) I don't think I really have a cantilever wall - It's a got a significant curvature to it, which going to stiffen it up and make it act in some ways like a braced wall. Now, for purposes of analysis, if I can prove the wall without counting on this self-stiffness, all good! But is there anything additional I should keep in mind in this situation, from a geotech perspective, as opposed to a typical flat cantilever retaining wall?