norzul,
The set up in your link is similar to the setup I have seen on my previous project.
In your blog, it seems that the SSOV is a self-contained unit (with it's own sensing lines). I like the fact that there are 2 in series.
In my system, we decided to go with 2 pressure transmitters going to a SIL rated safety system (separate from our DCS) and then to a shut off valve (in our case, a single valve).
The set-ups are similar.
Some notes:
We used 2 different brands of transmitters, and wired them separately (went to different JB and homerun cables) back to the safety system. The safety terminals in the JB are different colour from the DCS terminals, and segregated as well.
You may want to locate your sensing lines in different locations in the pipe (in case of fouling), and at least run them on separate side of the pipe back to the valves