From the NTSB report:
The National Transportation Safety Board determines that the probable cause of the July 10, 2006, ceiling collapse in the D Street portal of the Interstate 90 connector tunnel in Boston, Massachusetts, was the use of an epoxy anchor adhesive with poor
creep resistance, that is, an epoxy formulation that was not capable of sustaining long-term loads. Over time, the epoxy deformed and fractured until several ceiling support anchors pulled free and allowed a portion of the ceiling to collapse. Use of
an inappropriate epoxy formulation resulted from the failure of Gannett Fleming, Inc., and Bechtel/Parsons Brinckerhoff to identify potential creep in the anchor adhesive as a critical long-term failure mode and to account for possible anchor creep in the design, specifications, and approval process for the epoxy anchors used in the tunnel. The use of an inappropriate epoxy formulation also resulted from a general lack of understanding and knowledge in the construction community about creep in adhesive anchoring systems. In addition, Powers Fasteners, Inc., failed to provide the Central Artery/Tunnel project with sufficiently complete, accurate, and detailed information about the suitability of the company’s Fast Set epoxy for sustaining long-term tensile loads. Contributing to the accident was the failure of Powers Fasteners, Inc., to determine that the anchor displacement that was found in the high‑occupancy vehicle tunnel in 1999 was a result of anchor
creep due to the use of the company’s Power‑Fast Fast Set epoxy, which was known by the company to have poor long-term load characteristics. Also contributing to the accident was the failure of Modern Continental Construction Company, Inc., and Bechtel/Parsons Brinckerhoff, subsequent to the 1999 anchor displacement, to continue to monitor anchor performance in light of the uncertainty as to the cause of the failures. The Massachusetts Turnpike Authority also contributed to the accident by failing to implement a timely tunnel inspection program that would likely have revealed the ongoing anchor creep in time to correct the deficiencies before an accident occurred.
Dik